    We are considering using a DC
    current sensor in an upcoming product for Solar Inverters.

    Here are the requirements:
    * Ability to sense DC current from 1 to 10A, with 5% or better
    accuracy.
    * Bandwidth from 0 to 10Hz.
    * Must be able to withstand fault currents up to 300ADC.
    * UL listed or recognized preferred.
    * Operating range from -20 to 60C.

    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    09/04/2009 8:14 AM
    Dear Sir,
    Please review the spec sheet for our CR5200 Series. However, temp specs are a problem, these are based upon the accuracy of 1%. These should be able to operate -20 to 60 C and be within 5%. Accuracy is 1% 0 to 50C.