    I see that the 50:5 CT's have a lower accuracy than the 100:5 CT's. Specifically the CR2DA series. Would I achieve higher accuracy by using a 100:5 and passing the metered wire through a second time thereby creating a 50:5? My max current will always be less than 50A. Thank You.
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    02/10/2012 11:34 AM
    Dear Sir,

    Yes, I have attached our Field Adjustment of Current Transformer Ratio for your review.