    I have a Automation Direct PLC Do-06DR. DC inputs sinking or sourcing.

    I am switching 0VDC to the inputs and the +24VDC is connected to the input commons. I belive this means the inputs are sourcing.

    Which CR9321 current switch would I use? How would it turn on with only 0VDC at its input and the other wire going to the plc input?
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    12/20/2010 12:10 PM
    Dear Sir,

    Thank you for your interest in our product lines. The NPN output pulls the input low. You will need our CR9321-NPN for your application.