jim dayringerNew Member Posts:3
04/27/2010 6:19 PM |
|
I'm using a cr9350-aca to energize a small interposing relay with a 120V coil and power draw of 9ma. Will I need a snubber circuit? I found an old cut sheet for the cr9321-aca that showed a 2k ohm resistor and a .1uf capacitor as a recommended snubber. When I tried this it made the relay coil hum. The operation in either case was the same. Do I need the snubber to protect the current switch? Thanks
|
|
|
|
Tony HodgesCRM Staff Basic Member Posts:154
04/28/2010 11:01 AM |
|
Dear Sir, Thank you for the question. Please check and make sure you have enough current going throught he ring to activate the switch. Make sure you are not using a DC coil. From the specs you provided the unit should turn on without a snubber unit. You would need a snubber unit to turn it off. The recommended circuit is a resistor and capacitor in series across the wires of the device. A 0.01 microfarad capacitor rated 400 volts and a 100 ohm 1/8 watt resistor. I have attached our catalog page for your review with the wiring specs. There is a wiring diagram on the bottom. Please check to make sure it is wired properly.
|
|
|
|
jim dayringerNew Member Posts:3
04/29/2010 1:10 PM |
|
The switch will be used to sense current from woodworking tools. When I tested it, it seemed to turn on and off without any problems. The interposing relay coil is 120VAC with a 9ma power draw. Do I still need the snubber? Thanks
|
|
|
|
Tony HodgesCRM Staff Basic Member Posts:154
04/29/2010 2:33 PM |
|
You need a snubber unit to turn it off. The recommended circuit is a resistor and capacitor in series across the wires of the device. A 0.01 microfarad capacitor rated 400 volts and a 100 ohm 1/8 watt resistor.
|
|
|
|
Nathaniel TempestNew Member Posts:1
07/23/2018 12:35 PM |
|
I have a similar situation I'm designing for. Won't the parallel path across the switch allow some current flow even when its off? Can the snubber go across the relay coil instead?
|
|
|
|
Joe SchlerethNew Member Posts:4
07/24/2018 4:11 PM |
|
Hello Nathaniel, Thank you for your interest. There will be alittle current. However, the CR9350-ACA should turn off before 100mAAC and I would not imagine the current would be stuck above 100mAAC in a parallel path. In fact, you can use a snubber either across the secondary leads of the ACA CR9350 or across the relay.
|
|
|
|