3 phase 3 wire CT instal
 1 Replies
Sort:
Please register and login to participate in the forums.
Author Messages
Art Goodman
New Member
New Member
Posts:1


--
05/23/2013 12:25 PM
    I'm using the CR8350-2500-N current transformer to measeure 3 phase 3 wire system. I need to know the correct install for your CT. When H1 faces the source on L1 and L3, I get a Negative Active Power reading. When L1(H1) faces the source and L3(H1) faces the load my Active Power is Positive. Which way is the correct install.

    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    05/28/2013 8:27 AM
    Dear Sir,

    AC system phasing or polarity only applies when comparing two or more ac signals to each other. A single AC value on its own has no polarity. The standard assignment for our CTs is for the marked H1 side to be toward the source and away from the load. In this configuration, the output lead marked with the green dot and the “X1” will be the “positive” lead when compared to the driving voltage of the system. Please note that care must be taken to appropriately connect the 3 phase voltages in the right direction AND sequence for proper power system measurement.