Thuan Truong
New Member
New Member
Posts:3


--
06/03/2011 12:08 PM
    Dear Technical,

    I'm looking for the Phase angle error or phase shift, ratio error, standard Accuracy class, and nominal linearity %. Where can I get these info? Thank you.

    Best regard,

    Thuan Truong.
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    06/06/2011 9:47 AM
    Dear Valued Customer,

    Please provide your burden and input current. We will then be able to get this information for you.
    Thuan Truong
    New Member
    New Member
    Posts:3


    --
    09/13/2011 10:51 AM
    Dear Technical,

    I just get back to this project. I want to use the CR8350-2000 with the max input current is 100A and burden resistor is 1.7 Ohm. I just wonder is there a set up to get reply alert through email? Thank you.

    Best Regards,

    Thuan Truong.
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    09/13/2011 3:00 PM
    The CR8350-2000 has a DCR of 73 ohms and a turns ratio of 2000 developing a Vmax voltage of 31 volts. A 1.7 ohm resistor will cause a voltage level of 100/2000 * 1.7 or 85 mV. The transformer capability at that level of current is 31 – (100/2000)*73 or 31 – 3.65, or 27.35 volts. This application should be better than 0.5% accurate. You would still be linear using a resistor up to 27.35/100*2000 or 547 ohms for a 100 amp input.


    ---