CR5210-5
 1 Replies
Author Messages
Emma Liu
New Member
New Member
Posts:1


--
05/12/2017 2:31 PM
    The input range is 0-5ADC and output range is 0-5VDC, but I can get the output to go up to 14.15VDC and saturated after this. Is this normal?
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    05/24/2017 1:47 PM
    Thank you for your purchase. The output of the CR5200 Series is calibrated at 5Vdc of the full scale input. However, the output is not regulated to a maximum 5Vdc. So, if you input more than the full scale calibrated current the output will rise until the CT output is saturated.


    ---