Question on CR6260-500-5 Output Range
 1 Replies
Author Messages
Kalam Puckett
New Member
New Member
Posts:1


--
08/23/2013 6:24 AM
    We purchased the CR6260-500-5 to monitor the power of a 230V/3Ph motor with a power factor of 74%.

    I'm trying to determine the range of the 4-20ma output of the transducer. I'm making the assumption that 4ma (zero) is wattage at 0vac/0amps and 20ma (span) is wattage at 500vac/5amps. Then I'm thinking that the power factor would be applied in our DCS.

    Am I on the right track or totally off?

    Thank you in advance.

    Kalam Puckett
    Xcel Energy
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    08/23/2013 9:41 AM
    Dear Sir,

    The full scale output of the CR6260 will represent the amount of real power being used when 500 VAC and 5 amps AAC are being supplied to a PURELY RESISTIVE LOAD. The output will change and be accurate for different power factors, and thus is a measurement of the amount of real power that is being used in the load. Please refer to the attached pdf file for more information on this application.