I need to route the CT leads and the 480VAC lines to a near by cabinet for power monitoring. I will be using TSP wire for the CT leads. Should I run CT leads in a seperate conduit from the 480VAC lines or will the TSP wire be enough to prevent any interference on the CT leads?
Tony Hodges
CRM Staff
Basic Member
Posts:154
03/07/2013 12:07 PM
Dear Sir,
There will be no interference problem if the wires are run in the same conduit. The output of a CT is an ac current which will be relatively immune from electrical interference fields. Thank you for your business.