Calculate Compressor Current by using Power and Voltage Transducer
 3 Replies
Author Messages
Ahmed Abdulbaky
New Member
New Member
Posts:2


--
12/24/2012 1:01 PM
    Please I need Your Help in this Application , we need to Measure the Current Consumed by a Compressor From single Phase , But we only have a Power Transducer (Part# CR6210-250-20) and Voltage Transducer, so is it Possible To Calculate the Current From these Measurement ?

    Thanks
    Ahmed
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    12/26/2012 11:11 AM
    Dear Sir,

    You can calculate the effective current if the voltage is known. By itself, the CR6200 cannot tell you a current because the power is a function of current, voltage, and power factor. Thank you for your business.
    Ahmed Abdulbaky
    New Member
    New Member
    Posts:2


    --
    12/31/2012 1:41 AM
    thank you Sir,

    But what Does the Effective Current mean ?

    Thanks
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    12/31/2012 9:58 AM
    Dear Sir,

    Effective current is the value of the current for the power taken assuming it is completely resistive or zero power factor. Also known as active current. Typically less than actual current for non-zero power factor.


    ---