Current transducer CR5220
 1 Replies
Author Messages
Viktor Sokolov
New Member
New Member
Posts:4


--
07/30/2014 5:20 PM
    I like to install 2 CR5220 -(up to 30ADC first and up to 10ADC second)- on one DIN rail. Is there has to be some recommended distance between transducers to avoid any interference?
    Thank you.
    Tony Hodges
    CRM Staff
    Basic Member
    Basic Member
    Posts:154


    --
    07/31/2014 9:05 AM
    Dear Sir,

    Installing transducers close to one another does have some effect from the currents to be measured being in close proximity to one another at the measuring point. The question is to what degree. 10ADC and even 30ADC are relatively lower currents than hundreds, and also have a relatively minor cross talk with our transducers. The accuracy of 1% is not greatly affected. You could probably be safe mounting as close as comfortable wiring allows. However, if you are concerned, a good rule of thumb is 80 mm (3 inches) separation usually will minimize any crosstalk.


    ---